Adding a sub panel to garage
Don't let your house go up in Flames! Get it Right the First time!

Adding a sub panel to garage

CLICK HERE

Adding a sub panel to garage
Residential Wiring - The Right Way!

Wiring Information for the Do It Yourself Homeowner

Results 1 to 4 of 4

Thread: Adding a sub panel to garage

  1. #1
    Join Date
    Feb 2014
    Location
    Battle Creek, MI
    Posts
    2

    Default Adding a sub panel to garage

    I have a newer 100A service panel and am planing on running 6/3 copper about 60 feet to a small sub panel in my attached garage to add circuits there so I don't have to make several long 12/2, 10/2 runs to add what I want there. Yes I know most service panels are installed in the garage but mine is in the basement at the other end of the house which was built in 62. I plan on feeding it with a double 50A breaker but I have heard from some people on other forums that I can feed it with a 60A breaker. This does not seem right to me since 6awg is rated for 55A. Am I correct is saying that you can not use a double 60A breaker on 6/3 wire for 220V?

  2. #2
    Join Date
    Feb 2012
    Location
    Kent, WA
    Posts
    218

    Default

    If the calculated load for the subpanel is 55A or less, then you are allowed to "round up" to a 60A circuit breaker because 55A is not a standard breaker value. You can't apply this round up rule to multi-out branch circuits, but can on feeders under 800 amps. There are other exceptions that would allow an even larger breaker (e.g. a welder or large motor or compressor being fed by that panel).

    Seeing how many homes get wiring modified by handymen who don't know what they're doing (and don't do load calc), you'd be wise to limit yourself to the 50A breaker even though code will most likely allow it. You never know what a future homeowner will add...
    Mark
    Kent, WA

  3. #3
    Join Date
    Feb 2014
    Location
    Battle Creek, MI
    Posts
    2

    Default

    Quote Originally Posted by suemarkp View Post
    If the calculated load for the subpanel is 55A or less, then you are allowed to "round up" to a 60A circuit breaker because 55A is not a standard breaker value. You can't apply this round up rule to multi-out branch circuits, but can on feeders under 800 amps. There are other exceptions that would allow an even larger breaker (e.g. a welder or large motor or compressor being fed by that panel).

    Seeing how many homes get wiring modified by handymen who don't know what they're doing (and don't do load calc), you'd be wise to limit yourself to the 50A breaker even though code will most likely allow it. You never know what a future homeowner will add...

    Thanks for the help Mark. I just plan on adding a 20A circuit for outlets for general use and powered hand tools, a 30A RV outlet and maybe some more garage and exterior lighting powered by the sub panel. I will stick with a 50A breaker.

  4. #4
    Join Date
    Feb 2012
    Location
    Kent, WA
    Posts
    218

    Default

    Quote Originally Posted by hawkertech View Post
    Thanks for the help Mark. I just plan on adding a 20A circuit for outlets for general use and powered hand tools, a 30A RV outlet and maybe some more garage and exterior lighting powered by the sub panel. I will stick with a 50A breaker.
    Even a 30A circuit would work in this case -- RV on one leg and the lights/outlets on the other. So a 50A will provide plenty of growth.
    Mark
    Kent, WA

Similar Threads

  1. Garage frdige
    By Boman in forum Appliance Repair
    Replies: 3
    Last Post: 10-12-2016, 09:24 PM
  2. 2 red 1 white going to garage
    By taziskev in forum Electrical, Residential
    Replies: 5
    Last Post: 06-07-2015, 06:17 PM
  3. Magnetic fields, mains hum, and one quacky garage
    By relicpmg in forum Electrical, Residential
    Replies: 2
    Last Post: 02-21-2015, 12:28 AM
  4. Refrigerator in the garage
    By ninercub23 in forum Appliance Repair
    Replies: 1
    Last Post: 01-25-2015, 08:34 AM
  5. Adding a ground to my breaker panel
    By n4dou in forum Electrical, Residential
    Replies: 11
    Last Post: 01-04-2013, 03:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •